I explain what a economizer is on a chiller. These components are used to improve efficiency by increasing subcooling and in some cases removing the flash gas.
Chiller Training at chilleracademy.com
Troubleshooting Guides at hvactime.shop
TruTech Tools Promo: HVACTIME

Опубликовано:

 

22 июл 2024

Поделиться:

Ссылка:

Скачать:

Готовим ссылку...

Добавить в:

Мой плейлист
Посмотреть позже
Комментарии : 17   
@kc5vgw
@kc5vgw 12 дней назад
On the Trane cvhe and cvhf, the economizer does not pull into the suction. It is pulling into either the inlet of the second stage wheel, or 3rd wheel. Depending on if it’s a cvhe or f. On the york screws, the economizer is ported about 1.3 or 1.4x of suction. No appreciable loss as you can introduce more gas after the suction portion without adding any more load to the motor.
@Eighty8Fitter
@Eighty8Fitter 2 месяца назад
Refrigeration racks use subcoolers quite often. Improving efficiency is the overall name of the game.
@Ingmaringmar
@Ingmaringmar 2 месяца назад
In screw compressors the subcooler is connected to the eco port of te compressor, with a different (higher) pressure than suction pressure. (This is where the efficiency gain is). How is that for centrifugal compressors?
@kc5vgw
@kc5vgw 12 дней назад
Same with a centrifugal, provided it has more than 1 stage. York yt and yk, as well as yz and YMC2 are only 1 stage of compression. However Trane uses multiple stages. And the york OM’s are multistage. Between 2 and 5 stages. Only seen 5 stage in the refineries. Usually for the PDU. Propane de asphalting unit. And they are almost always R-290 systems
@HVACGUY
@HVACGUY 2 месяца назад
Gree flexx hs those before liquid line to add subcooling.
@isaiahlewis3832
@isaiahlewis3832 2 месяца назад
What’s making the vapor rise to the top of the flash tank ?
@HVACTIME
@HVACTIME 2 месяца назад
Vapor is less dense than liquid. Vapor rises on top and the liquid collects in the bottom.
@isaiahlewis3832
@isaiahlewis3832 2 месяца назад
The condenser is sending liquid refrigerant to the flash tank how is that liquid being turned into a gas ? & does it has something to do with pressurization or expansion and how ?
@HVACTIME
@HVACTIME 2 месяца назад
Through a expansion valve. There is a expansion valve prior to the flash tank that creates the flash gas.
@isaiahlewis3832
@isaiahlewis3832 2 месяца назад
Thank you so much & when u say create the flash gas that means changing the state correct ?
@HVACTIME
@HVACTIME 2 месяца назад
@isaiahlewis3832 correct, charging state
@Skunkhunt_42
@Skunkhunt_42 15 дней назад
Yes ​@@isaiahlewis3832
@irfvnfaedah5776
@irfvnfaedah5776 2 месяца назад
Sr ,may u help me, on york yciv Is there the High pressure cut out at system 1 is serial with system 3 on logic board
@kc5vgw
@kc5vgw 12 дней назад
Yes. I think it’s due to a limitation of the digital inputs on the boards.
@NROhvac
@NROhvac 2 месяца назад
Is it ok to think chiller economisers are similar to hot gas bypass, by the concept of keeping a load on the chiller?
@HVACTIME
@HVACTIME 2 месяца назад
No, different concept
@NROhvac
@NROhvac 2 месяца назад
@@HVACTIME ok I understand thank you
Далее
Why does Discharge Superheat Matter?
12:27
Просмотров 2,9 тыс.
York Chiller Refrigeration Cycle - YCIV & YVAA AC
30:38
This or That 🛍️
00:52
Просмотров 9 млн
You're wasting money on heating! Use your A/C!
17:11
Просмотров 395 тыс.
Secret to Master Tech & MY GAME
13:46
Просмотров 3,6 тыс.
HVAC VFD compressor fault!
21:17
Просмотров 494
Tripping Low Pressure York Air Cooled Chiller Down
26:01
Trane Chiller Centrifugal Refrigeration Cycle
43:22
Просмотров 50 тыс.
YK Overview Centrifugal Chiller York HVAC Training
27:47
First 5 Steps to Troubleshoot Chillers
12:57
Просмотров 3,6 тыс.
DX vs Flooded: Chiller Evaporator Types
10:12
Просмотров 1,4 тыс.
This or That 🛍️
00:52
Просмотров 9 млн