DIY Solar Forum Question. Will the EG4 6000XP work from a single 120v generator or Grid connection? 

The Adventures of a Renaissance Man
Подписаться 582
Просмотров 6 тыс.
50% 1

Affiliate links below
Signature Solar Site - signaturesolar...
EG4 Communication HUB - signaturesolar...
18Kpv AIO - signaturesolar...
6000XP AIO - signaturesolar...
LifePower 4 Battery - signaturesolar...
LifePower 4 Server Rack - signaturesolar...
48v ChargeVerter - signaturesolar...
LL S v4 Battery - signaturesolar... DIY Solar Forum Question. Will the EG4 6000XP work from a single 120v generator or Grid connection?
Short Answer Nope.
Affiliate links below
(I'm Brand new to this affiliate stuff)
Using links below will (I hope) support my Solar Addiction.
Signature Solar Site - signaturesolar...
EG4 Communication HUB - signaturesolar...
18Kpv AIO - signaturesolar...
6000XP AIO - signaturesolar...
LifePower 4 Battery - signaturesolar...
LifePower 4 Server Rack - signaturesolar...
48v ChargeVerter - signaturesolar...
LL S v4 Battery - signaturesolar...

Опубликовано:

 

15 сен 2024

Поделиться:

Ссылка:

Скачать:

Готовим ссылку...

Добавить в:

Мой плейлист
Посмотреть позже
Комментарии : 103   
@sreimert
@sreimert 3 месяца назад
I think this would work if you wired it like this: The generator's 120V output (hot wire) would be connected to both the L1 and L2 input terminals on the EG4 6000XP. The generator's neutral wire would be connected to the inverter/charger's neutral input terminal. The generator's ground wire would be connected to the inverter/charger's ground input terminal.
@Madsci-zy8wm
@Madsci-zy8wm 6 месяцев назад
No, it won't work, unless you use a step up transformer. Not only won't it work from a single 120v generator or Grid connection, but because of it's low surge capacity, (only 200%) it won't start or run a single 6kW inductive motor load. In order to start a single 6kW motor load, you would need a heavy duty, low frequency, transformer based inverter charger.
@theadventuresofarenaissancman
@theadventuresofarenaissancman 5 месяцев назад
Sounds accurate.
@michaelambrosia
@michaelambrosia 2 месяца назад
trying the trandformer and no response. Apparently, it needs to receive split phase. Trying to figure this out after signsture solar tech lacked the knowledge to help with a solution.
@chicagoterence
@chicagoterence 5 месяцев назад
Well, this is wired wrong. If you wire correctly it will show 120V... however still does not charge... and yeah, signature solar assured me it would. Needs to be true 240 split phase too btw.
@michaelambrosia
@michaelambrosia 2 месяца назад
I'm wondering if it would work with a transformer running two forty single phase?
@Adrayven
@Adrayven 9 месяцев назад
Curious, my first thought was, why was the neutral not connected to the neutral.. Why would you connect it to the L2 hot? that makes no sense for this test... I cannot think of any instance where you'd connect the neutral to the second hot.
@theadventuresofarenaissancman
@theadventuresofarenaissancman 9 месяцев назад
Agreed. I'm told that some inverters (growatt and victron) have a grid input range of 120 or 240. I suspect those specific inverters have a transformer.
@theadventuresofarenaissancman
@theadventuresofarenaissancman 9 месяцев назад
See comment and reply from other person.
@DaRoach5882
@DaRoach5882 3 месяца назад
Hey, I know this is from 5 months ago but I was able to get 120v charging to work with mine I don't know if it was a firmware change or not but its working now. Connection I used was Hot on line 2 and Neutral on Line 2. and I was able to charge. Note that the output while on the grid was not correct as it was only 60 volts from line to neutral. The other thing that I noticed was that I needed around 650 watts or more of charging to get it to work
@michaelambrosia
@michaelambrosia 2 месяца назад
Hot online 2 of grid?? And neutral online 2 of generator? I'm currently trying to figure this problem out as well
@michaelambrosia
@michaelambrosia 2 месяца назад
trying the transformer and no response. Apparently, it needs to receive split phase. Trying to figure this out after signsture solar tech lacked the knowledge to help with a solution.
@michaelambrosia
@michaelambrosia Месяц назад
Transformer did not work because this inverter requires split phase.
@wkc073406
@wkc073406 20 дней назад
@DaRoach5882 I'm surprised you were able to get this to work. All accounts it needs split phase.
@bowbilly9080
@bowbilly9080 8 месяцев назад
My Schneider Conext SW 4024 Inverter/Charger will enable the charger to charge the batteries with 120v or 240v input. I have used my 120v generator and my larger 240v generator. But when you use 120v the inverters charger output is reduced by 50%. You an also set the input amperage limit to prevent tripping the circuit breaker for the generator. I am completely off grid so no way to test it with grid power. But sure it would work the same. There is only one A/C input on the inverter and not two separate inputs, one for generator and one for grid power. Documented really well in the manual. It will even load support if a heavy load comes online by cutting the battery charger off and assisting the generator power the load with inverting power from the batteries. Then when the excess load stops it will return to charging the batteries again.
@theadventuresofarenaissancman
@theadventuresofarenaissancman 8 месяцев назад
It would be nice if that kind of information was more obvious to buys that need the flexibility of 120 and 240 charging.
@tjmooney4181
@tjmooney4181 3 месяца назад
Can i wire a honda 6500 240v generator into the generator input of the 6000xp to avoid using a chargeverter?
@theadventuresofarenaissancman
@theadventuresofarenaissancman 3 месяца назад
Sure, one question does the Honda have that weird setting where it can parallel the two outputs in to a single 120v?
@tjmooney4181
@tjmooney4181 3 месяца назад
@theadventuresofarenaissancman nope just a 14-30 4 prong twist lock I planned to cut one end off the extension cord and wire into the gen input but couldn't figure out if it would work correctly if I just turned it on and off when I choose instead of hooking up the auto start dry contacts
@theadventuresofarenaissancman
@theadventuresofarenaissancman 3 месяца назад
@@tjmooney4181 sounds like it should work. I don't remember if the 6000xp will default to charging batteries with the newest firmware. You may need to adjust the XP generator settings so it will always charge when the generator is running. But that's easy.
@tjmooney4181
@tjmooney4181 3 месяца назад
@theadventuresofarenaissancman thanks so much for the quick responses I planned to follow your other video about generator settings to set at 5000 watts for this generator. I am using 1 6000xp and 1 powerpro for this project
@michaelambrosia
@michaelambrosia 2 месяца назад
trying the trandformer and no response. Apparently, it needs to receive split phase. Trying to figure this out after signsture solar tech lacked the knowledge to help with a solution.
@zachreyhelmberger894
@zachreyhelmberger894 8 месяцев назад
HOW do you turn on the generator relay? I have 6 Lifepower4 batteries at about 15% SOC and blinking red led alarm. Is there ANY possible way to charge these batteries using the 6000XP?
@theadventuresofarenaissancman
@theadventuresofarenaissancman 8 месяцев назад
Yes, Have you changed the generator settings using the APP or Website?
@theadventuresofarenaissancman
@theadventuresofarenaissancman 8 месяцев назад
Give me 1-2 hours, I'll throw together a video walking through the generator settings using the Android App.
@theadventuresofarenaissancman
@theadventuresofarenaissancman 8 месяцев назад
Almost done. Should be published in 20 minutes.
@SmartBusN
@SmartBusN 7 месяцев назад
so I have the eg4 3kw right now in a rv and when the solar is bad uses grid when I'm plugged in. so I'm about to buy this inverter it will only charge the batteries and bypass with a 30 amp plug outlet? it won't work if I put an adapter on the 50-amp plug down to a 120v when you go to some campgrounds or families house that don't have a 30 amp or 50-amp outlets? Because the eg4 3kw works on fine on i just have the settings for charging turned down to 15amps so it won't trip the breaker. I just want to be clear on this because even on my old electric system the on rv will run on 120v with the adapter just don't run 3 things at once or ac units. My rv 2003 model so tech was older and would auto switch. The eg4 3kw is wired up 30-amp wire and outlet when I have 30-amp service I turn up the charge to 30amp in setting. so I'm curious if you wire it up 50 amp and use an adapter will it work good next video just remember turn the charge amperage down or you will pop the breaker found that out day 1 then I read the manual for days memorized it.
@theadventuresofarenaissancman
@theadventuresofarenaissancman 5 месяцев назад
The 6000XP would need 240v (50 amp)
@electronicwizardsolartech
@electronicwizardsolartech Месяц назад
Hi, have you connect the 6000Xp to a single phase 240 volts ?
@theadventuresofarenaissancman
@theadventuresofarenaissancman Месяц назад
Yes but that was 6 - 8 months ago. I haven't tried recently.
@theadventuresofarenaissancman
@theadventuresofarenaissancman Месяц назад
If my memory is accurate the XP checks for voltage at L1 to N, L2 to N and L1 to L2 and will disconnect from grid if either voltage is out of range.
@igowhereimtowed6839
@igowhereimtowed6839 7 месяцев назад
Did you try 120 into L1 and jumper L1 to L2. White to the N bus. Then change setting #13 AC In: AC Voltage Range Setting. Change to APL - 90 - 280VAC. Per Technical Specifications, AC Input Data, Nominal AC Voltage 120 - 240VAC If jumping L1 to L2, didn't work, how about 120 to just L1.
@theadventuresofarenaissancman
@theadventuresofarenaissancman 7 месяцев назад
Jumping L1 to L2 results in the inverter seeing 0 volts. It doesn't care what the voltage between L1 to N. The inverter only displays L1 to N voltage for the end user.
@igowhereimtowed6839
@igowhereimtowed6839 7 месяцев назад
@theadventuresofarenaissancman does changing program settings #13 AC In: AC Voltage Range Setting. Change that to, APL - 90 - 240VAC. Make any difference?
@theadventuresofarenaissancman
@theadventuresofarenaissancman 7 месяцев назад
No it doesn't appear to. It would need to to go down to 50v to work.
@christophersmolinski6194
@christophersmolinski6194 4 месяца назад
Did you try a jumper between L1 and L2? Some units simply need to see 120v OR, does it need to truly be a split phase 240v?
@theadventuresofarenaissancman
@theadventuresofarenaissancman 4 месяца назад
From my testing, it needs a true 240v
@zachreyhelmberger894
@zachreyhelmberger894 8 месяцев назад
Let me see if I got this right: YOU CANNOT USE A 120V GENERATOR WITH THE 6000XP. Am I reading this right? Even if you connect the neutral to the neutral bus bar?
@theadventuresofarenaissancman
@theadventuresofarenaissancman 8 месяцев назад
Correct. 120v is well below the minimum cutoff voltage. I'm not certain but I think the minimum voltage is 180v when measured between L1 and L2
@peamealprosciutto2454
@peamealprosciutto2454 7 месяцев назад
my generator has a 20 amp and a 30 amp outlet, what about running one hot from each as l1 and l2. would they be in offsets phase then ?
@theadventuresofarenaissancman
@theadventuresofarenaissancman 7 месяцев назад
Very rare to find a generator that has split-phase 240v that doesn't have a 240v plug. I suspect no it wouldn't work.
@lancealderman2755
@lancealderman2755 7 месяцев назад
120v into rectifier and then into solar input and set charging current to battery under the generator's rated capacity... I wouldnt do it with such an expensive piece of equipment however Im fairly certain it would work 😅
@theadventuresofarenaissancman
@theadventuresofarenaissancman 6 месяцев назад
Thats one way to do it.
@ramonseda
@ramonseda 2 дня назад
This was added in the latest firmware.
@Espiritiv
@Espiritiv 4 месяца назад
Damn so you cant make a portable generator cart with the 6000XP like you can with the 3k and just charge it with 120V 20A plug? I was hoping i could so some slow charging on my wall outlet and then have 240V available for running some loads in a pinch. Sounds like i am going to have to pick up the 3K instead
@theadventuresofarenaissancman
@theadventuresofarenaissancman 2 месяца назад
That sure would be nice. Someone mentioned using 2,000 or 3,000 watt 120/240 transformer and setting AC charge at a lower amperage
@michaelambrosia
@michaelambrosia 2 месяца назад
Thanks for sharing. I wish they would put this on their website or in the manual, because I just found out the same thing after spending a lot of money on this stuff. Next i'm thinking about using a transformer... Have you went down that route?
@theadventuresofarenaissancman
@theadventuresofarenaissancman 2 месяца назад
No, but I heard someone used a 3000 watt 120 to 240 transformer from Amazon.
@michaelambrosia
@michaelambrosia 2 месяца назад
​@@theadventuresofarenaissancman trying the transformer and no response. Apparently, it needs to receive split phase. Trying to figure this out after signsture solar tech lacked the knowledge to help with a solution.
@johnmcadaragh694
@johnmcadaragh694 8 месяцев назад
Im trying to figure this out as well. What about a 120 to 240 step up converter? Would add some efficiency losses but seems like it would work.
@theadventuresofarenaissancman
@theadventuresofarenaissancman 8 месяцев назад
Almost cheaper to buy a Chargeverter.
@johnmcadaragh694
@johnmcadaragh694 8 месяцев назад
@@theadventuresofarenaissancman well amazon has the converters for $50-100 depending on your wattage requirement
@theadventuresofarenaissancman
@theadventuresofarenaissancman 8 месяцев назад
I just priced out auto transformer in the 3000-6000 watt range and they are priced well above $1,000. What are you looking at?
@johnmcadaragh694
@johnmcadaragh694 8 месяцев назад
@theadventuresofarenaissancman oh I guess youtube deletes amazon links. If you go there and search 120v to 240v converter, you'll see a bunch
@Brisket9392
@Brisket9392 8 месяцев назад
@@johnmcadaragh694 Test the Vevor Voltage Converter Transformer. $50 for 3000W after coupon.
@nabilali3230
@nabilali3230 6 месяцев назад
I have a question. Is it possible to use a single 240v leg?
@theadventuresofarenaissancman
@theadventuresofarenaissancman 6 месяцев назад
Yes single phase 220. I don't have any way to verify but yes it should work.
@PanelsUpSolar
@PanelsUpSolar 9 месяцев назад
Why are you connecting the neutral to the hot leg. Would it not need to go to the neutral bus?
@theadventuresofarenaissancman
@theadventuresofarenaissancman 9 месяцев назад
This video was only intended to address a reoccurring question on the DIYSOLAR forum.
@PanelsUpSolar
@PanelsUpSolar 9 месяцев назад
@@theadventuresofarenaissancman But if it was hooked up correctly would it have worked? I am only asking because I don't know. I have a bunch of experience with the Victron stuff and charging from a single phase generator is no issue at all.
@theadventuresofarenaissancman
@theadventuresofarenaissancman 9 месяцев назад
@PanelsUpSolar the 6000xp require 240 split-phase from Grid or Generator. The AC pass-through and/or AC charging will not work with any combination of a single 120v. Same applies for Generator input.
@garrickgaffigan4522
@garrickgaffigan4522 9 месяцев назад
If that's the case it's useless to me and SS will be getting it back. I don't have a 240 generator. And they should have mentioned that since I sent my installation plan to them
@robdabiere651
@robdabiere651 8 месяцев назад
You are correct. For a small system it should accept a 120 charge, people who are buying these don't usually use 240 for anything so why would they have access to a 240 generator.
@neemaborji9993
@neemaborji9993 7 месяцев назад
I just found this out recently too. 6000xp cannot use 120V from a generator for charging. It only accepts 240v from the generator. You would need an eg4 chargeverter to charge from 120V generator 😢
@theadventuresofarenaissancman
@theadventuresofarenaissancman 7 месяцев назад
Correct.
@kurtleyendecker134
@kurtleyendecker134 6 месяцев назад
So Last weekend I set up my 6000xp not knowing it would not charge the batteries using 120v from the Grid connection. BUT after fooling around with the settings bit, the inverter decided it was connected to 240v and began charging on 120v. This session lasted about 6 hours and charged the batteries 3.1kwh. I had to shut things down for the night given temps were predicted to drop below 32 F. I have not been able to replicate this since. Incidentally, the hot was connected to L1 and the neutral was connected to the neutral bus. Why did this work? We may never know. What this tells us, however, is the 6000xp is perfectly capable of charging in 120v but it is hobbled by the controller and likely the controller's firmware. Incidentally, when I was trying to get the inverter to repeat 120v charging, my screen would report 120v on Grid 1 (L1), but curiously, 12v on Grid 2 (L2). Nothing was or is connected to the Grid L2 connection. Don't know what this all means but thought I'd share this.
@theadventuresofarenaissancman
@theadventuresofarenaissancman 6 месяцев назад
I have a feeling that it's just a firmware limitation.
@theadventuresofarenaissancman
@theadventuresofarenaissancman 6 месяцев назад
Thank you for sharing
@irfanwaseh
@irfanwaseh 8 месяцев назад
Can it work with out batteries and grid pass through ?
@theadventuresofarenaissancman
@theadventuresofarenaissancman 8 месяцев назад
I haven't tested without batteries. The user manual says it can. Your solar needs to supply all of your load, if solar input is insufficient, the inverter falls back to grid bypass.
@theadventuresofarenaissancman
@theadventuresofarenaissancman 8 месяцев назад
Check out this video. He simulated a no battery test with three 6000xp. ru-vid.com/video/%D0%B2%D0%B8%D0%B4%D0%B5%D0%BE-PN7l704Cjlk.htmlsi=XCih3Ij5VUVEguNg
@Mike-01234
@Mike-01234 7 месяцев назад
Can the 6000xp power the load from PV/battery/AC All 3 ? I want to power a 4 ton AC unit with 4000W of solar 15kw of battery. I know it won't be able to power it completely it will need some grid to help. Is that possible? The AC unit has a microair softstart. Watching your videos seems like it is possible when I called SS or EG4 both give different answers. EG 4 said no you get one or the other like a light switch. SS said yes it will work that way because way these work. After watching some of your videos seems like it is possible to adjust how much power is coming from the grid at lease manually. I suppose at night when the battery dies I would want 100% from the AC grid at some point.
@theadventuresofarenaissancman
@theadventuresofarenaissancman 7 месяцев назад
No, this is an offgrid inverter. You will need a grid interactive inverter. Like the 18Kpv. Or you will need additional 6000xp in parallel.
@theadventuresofarenaissancman
@theadventuresofarenaissancman 7 месяцев назад
Well, technically during an overload the inverter will fall back to grid. So it could work, but remember the grid is all or none and switching back and forth would add extra wear to household electronics.
@Mike-01234
@Mike-01234 7 месяцев назад
@@theadventuresofarenaissancmanCan't the grid and PV charge the batteries? Looked like there was a way to control how much grid power is used for charging. During that time the load is running off the battery.
@theadventuresofarenaissancman
@theadventuresofarenaissancman 7 месяцев назад
Yes and no. When grid is charging the batteries, the load will be powered by the grid.
@Mike-01234
@Mike-01234 7 месяцев назад
@@theadventuresofarenaissancman That would be true if you can't limit the amount of current from the grid. I suppose trying to adjust it based on solar output not that easy.
@wkc073406
@wkc073406 20 дней назад
Chargeverter needed.
@theadventuresofarenaissancman
@theadventuresofarenaissancman 20 дней назад
Basically
@varman001
@varman001 5 месяцев назад
Dude wire the neutral(white) to the neutral bus bar NOT to L2, it will work! also it will work if you get an extensions from each leg(that would be 2 extension cords) and connect them together, you will see 240v.
@theadventuresofarenaissancman
@theadventuresofarenaissancman 5 месяцев назад
This was a demonstration, answering a reoccurring community question.
Далее
EG4 6000XP, Explaining how the generator settings work.
11:27
Merab vs Sean underway!! 🚨 #ufc306
00:23
Просмотров 884 тыс.
The REAL Problem with Smart Meters
20:05
Просмотров 423 тыс.
EG4 6000XP + Power Pro Indoor 48V Battery Install!
9:30