When using ACCA's Manual T for register selection, there are several basic rules that are followed regarding location. Most guidelines revolve around room air circulation and stagnant air, as well as the equipment application (heating only, cooling only, or combination). Application is the largest determining factor when it comes to return air locations.
Chris Morin is the Author, Owner & Founder of the popular HVAC Pro Blog. For Advice with Residential HVAC System Design, Quality Installation, and System Diagnosis, you can find Chris' Articles on HVACProBlog.com, Exclusive Member Content on Patreon, or popular social media outlets Facebook, LinkedIn, Twitter and RU-vid.
- Royalty Free Music from Bensound

Опубликовано:

 

26 июн 2021

Поделиться:

Ссылка:

Скачать:

Готовим ссылку...

Добавить в:

Мой плейлист
Посмотреть позже
Комментарии : 29   
@wayneschneyer8699
@wayneschneyer8699 2 года назад
Thanks for another very good and helpful video. As a retired 50 year veteran of the HVAC industry I have found many contractors are sorely undertrained or just unprofessional. But for the pros I offer this: Many times customers are only interested in price. This becomes a brick wall when the previous estimates never mentioned duct repairs( getting the bad hi equivalent fittings out) or duct sealing. When the professional starts talking about this, the customer shuts down thinking this is just a way to inflate the price. Helpful in many cases is the great consumer oriented literature given out by the US Government. US Dept. of energy / energy star program. The great brochures are free you so you leave the brochure with them. It’s a simple fact sheet showing how the duct system and proper installation, duct sealing all make up the real system efficiency; it’s no longer you, the profit driven contractor, saying these things are important but rather The US Dept of Energy. Credibility! I’ve seen where this third party verification of what your saying sways the customer to your side, even with the price being higher than the others. I was sealing up duct systems as an option ( extra charge ) back in the 70s after the first Arab oil embargo. Consumers need more education from professionals to make an “ informed decision” Thanks.
@jimenez3053
@jimenez3053 Год назад
Great video Sgt! I served from 4-2003 to 4-2007. Two tours in Iraq.
@user-vt2vd4ek4b
@user-vt2vd4ek4b 4 месяца назад
What did you get other than killing ppl u will be asking by God when you meet him
@perpetualengine
@perpetualengine 2 года назад
Down in Georgia after living in Mass all my life. Cooling is not keeping up even though the units are large enough. I mentioned raising the return on the 3rd floor. (The return is on the loft floor and the peak is 13ft above that) my HVAC guy said to get higher flow filters, under cut the bedroom doors and for filtration, buy his friends stand alone water air filter. I have like 5 weeks of winter down here, I'm going to put my return as high as possible.
@poli21
@poli21 2 года назад
Brilliant. Thanks so much.
@hvacgameproper1177
@hvacgameproper1177 3 года назад
50% of my change outs in Philadelphia I propose completely changing the basement ductwork. Most of the ductwork is from legacy gravity/slow moving air flow systems.
@HVACProBlog
@HVACProBlog 3 года назад
Yes! Low velocity will create tremendous issues with trying to retrofit existing 'gravity' type duct systems with today's systems...condensation, mold/mildew, and an uncomfortable homeowner will all result. A room x room load calc, then Duct Run/trunk worksheet should be completed to verify the distribution will work with the new system, EVERY TIME! The trouble is, if you are doing this right, somebody will always come in lower, not fixing/replacing the duct system. Customer education early in the Sales Process is essential...Good Luck in Philly!
@munyaradzimuchacha
@munyaradzimuchacha 2 года назад
Hey Martin This is very useful. In a double storey home which is the best location
@gregburns8099
@gregburns8099 Год назад
I have been a rough-in installer in residential new construction in KCMO for nearly 20 years. Trying to move into layout and design of new construction. I've always been taught that supply and return should be opposite. If supply is high, return is low and vice versa. We have nearly even heating and cooling seasons. Should I be more concerned with the requirements of each level? Cooling more on second floors? Heating more on lower levels?
@rodralph824
@rodralph824 Год назад
My townhome place in Florida uses mostly cold AC. There is a large floor level return air filter and grill at the bottom of the upstairs hall that feeds the ambient air directly into the AC unit and air handler. There are also ceiling return air vents in most rooms upstairs and down. Where are these vents supposed to return the air? I have seen a lot of talk about these vents but nobody bothers to say where they return the air. Appreciate you help. Rod, Vero Beach
@JB-yq9bn
@JB-yq9bn Год назад
Low return in heating only, only makes sense if you have a large soffit in walls. 3.5 inch that also has to be internally insulated riser box in a 2x4 wall dosent work going down a 8 foot wall. The ceiling would still be better with a unit in an attic.
@GregoryGuay
@GregoryGuay 5 месяцев назад
I have two supply ducks in my home theater and realize I need to add a event to relieve the static pressure buildup - so it technically won’t be a return - but I will add a baffle box with a vent that recycles the air close to the return outside of the room. My question is this, is it OK to put The exit vent on my knee wall instead of the ceiling? I live in the south, so I definitely want heat to leave the room.
@tuckerhigley6997
@tuckerhigley6997 Год назад
Why isnt there tech so you can have both but an actuator closes it in the middle depending on if it’s on cool or heating mode. 😂
@azncooler
@azncooler Год назад
How do you apply a down low return in California if I don't have a basement for a furnace?
@jasonbreding7905
@jasonbreding7905 Год назад
Would you ever spray foam over hvac ? We did and is it dangerous
@8683roy
@8683roy Год назад
Is there a formula for an air return duct size in relation to the supply size in a small sealed room? In other words I will be supplying a room with 2- 6" ducts. What should the return air size be?
@ross2343
@ross2343 2 года назад
Question: I'm changing out my bi-fold louvered door (in front of hvac closet) for a single swing out louvered door; is there a code or general rule of thumb for recommended space size between the slats? I heard the thickness of a pencil is a good rule of thumb..there are no return ducts....thanks
@HVACProBlog
@HVACProBlog 2 года назад
Hi Mark! The space needed is based on the pressure difference between the rooms. There should be less than a +/- 5 pa difference. If there is a return and supply in both areas/rooms, then the need for louvered doors for the purpose of comfort is diminished (still needs to be balanced). Basically, if the louvers are adjustable, then open until the pressure differential is within 5pa. Same goes for the amount of 'undercutting' a door, or sizing a jump duct. Most open the door until the pressure is equal between spaces, then calculate the free area needed by measuring the door opening (lets say you opened 3", then 3"x60"=180 sq.in.). Hope that helps?!
@HVACProBlog
@HVACProBlog 2 года назад
Almost forgot - if you have a combustion appliance like a furnace or water heater in that closet - the amount of combustion air needed should be accommodated! Turn on both appliances and complete the same test, making sure you are within 5pa.
@kr5289
@kr5289 Год назад
Our Sunday school room stays hot unless we cracked the door about 2 inches if I install a 12x12 grill up high would this make a difference the room is small and we don't like leaving the door cracked due to noise. Thanks
@HVACProBlog
@HVACProBlog Год назад
Great question KR - installing a 12"x12" register in a drop ceiling (I assume) could fix this problem for you - as long as the system has an open plenum return, pulling air from above the ceiling. The free area of this register roughly matches your 2" gap for a 72" height door. The returns may be ducted to your hallway though, and if not taken from above the ceiling with an open plenum, would mean the register would have to be ducted back to your return trunk...Good Luck with your classroom!
@SimonPhoenix2022
@SimonPhoenix2022 Год назад
My apartment has a fresh air vent. It's just a 10x10 return register with a duct that leads outside. It has a filter what direction should the airflow arrow point? Into the apartment or towards the ceiling? They had it facing the ceiling shouldn't it be filtering the air coming into the apartment?
@thenexthobby
@thenexthobby Год назад
If it's _returning_ to the system, you're correct of course. [Edit] Your fresh air vent is a "make up vent," used to supply the HVAC with fresh outside air. You can achieve load balancing with out it (because that's a different topic) so if we ignore for the moment how it's different ... it's similar to the returns. Meaning, you have supply ductwork, you need corresponding return ductwork that draws air either from inside the house or outside. There are humidity and heat implications with both solutions, and one isn't a substitute for the other.
@shirleypineda9726
@shirleypineda9726 3 месяца назад
If I have a return air in my wall and with no ducts leading like literally just a return vent and then you see the inside of my walls. Why? My house was built in 1988.
@HVACProBlog
@HVACProBlog 2 месяца назад
Hi @shirleypineda9726 ! Thanks for watching my content. Although ok at the time (1988), this is using the wall cavity as your return duct and would not meet today's installation codes. The wall cavity is extremely leaky and will be taking more air from unwanted areas, not only from your conditioned space...
@dm7175
@dm7175 12 дней назад
Dude, where the f#%$ is the vent?
@jaedenspider877
@jaedenspider877 Год назад
My old house has the worst HVAC system
@darkflux
@darkflux 4 месяца назад
dude, you need to fix your audio sync and reupload. i'm sure your information is accurate and very helpful, but i can't watch that out of sync mess. and that background music...just unnecessary. if you're going to be a content creator, you need to know what you're doing. or hire somebody who does.
@HVACProBlog
@HVACProBlog 4 месяца назад
Thanks for the feedback. This video is almost three years old and I have corrected many of your issues identified. Please consider checking out some of the newest content?
Далее
Manual D - Rules of Duct Design
6:55
Просмотров 29 тыс.
3 HVAC Ductwork ISSUES Homeowners NEED To Know!
8:06
Просмотров 373 тыс.
Fast and Furious: New Zealand 🚗
00:29
Просмотров 22 млн
Воскресный утренний стрим!
1:00:16
Basic Return Duct Sizing Made Simple
5:28
Просмотров 366 тыс.
Adding Return Air for Bedrooms (easy)
8:55
Просмотров 59 тыс.
My DIY Geothermal System Was So CHEAP!!!
19:35
Просмотров 2,8 млн
Residential Ductwork : HVAC Duct Design Basics
6:34
Просмотров 135 тыс.
How does the air conditioner work?
7:26
Просмотров 2,8 млн
Stop Sweaty Ducts, Vents and Systems
23:26
Просмотров 240 тыс.
Fast and Furious: New Zealand 🚗
00:29
Просмотров 22 млн