This is a basic guide for calculating the number of lights you can have on a single circuit.
Thanks for watching and subscribing! As an Amazon affiliate I earn from qualifying purchases. Thank you for your support!
0:00 - How Many Lights On A Breaker Intro
0:19 - Formula To Find Watts
1:00 - Maximum Continuous Circuit Load
1:32 - How Many Lights On 15A Breaker?
2:26 - What If They Were LEDs?
3:02 - Why Not To Use A Single Breaker
4:05 - SUBSCRIBE!!!
Blessings,
Ben

Опубликовано:

 

21 июл 2024

Поделиться:

Ссылка:

Скачать:

Готовим ссылку...

Добавить в:

Мой плейлист
Посмотреть позже
Комментарии : 489   
@TannerTheGreat0
@TannerTheGreat0 5 лет назад
I've been an electrician for 6 years now and this guy has solid knowledge, and excellent teaching qualities. I always recommend my coworkers to these types of videos to help learn the more in depth side of electrical distribution and code. Keep up the great work man!
@mikelarry2114
@mikelarry2114 4 года назад
I watch 30 videos trying to understand what u said in 4 mins. You broke it down so easily for newbies!! Thank you so much!
@jimproffer570
@jimproffer570 3 года назад
Except that the 80% rule doesn't apply to most household loads, lighting included.
@adriancastillo1143
@adriancastillo1143 3 года назад
question i have a customer that previously had a small shed wired. she is saying that sometimes the power turns off. its on a 15amp breaker. grounded to a panel in the shed that has other breakers on it. will a 20amp breaker fix that problem? short of rewiring her whole shed. also her shed as multiple plugs and switches. I was thinking it was just drawing to many amps.
@glasshalffull8625
@glasshalffull8625 Год назад
@@adriancastillo1143 Does it trip when she’s running her arc welder or some similar high amp device? Since it’s a small shed, I would kill the power and then check every connection to make sure there’s not a loose one and also the breaker connection. If it’s not an obvious fix, then maybe replace the breaker as it might be failing.
@glasshalffull8625
@glasshalffull8625 Год назад
@@jimproffer570 So what is the correct percentage and an explanation would be nice?
@zazenmonkey945
@zazenmonkey945 5 лет назад
Ben, thank you for your videos. The first thing I notice and like about your videos is the style of electrical work you display, very clean, very ordered, very professional; even though 99.9% of it will be hidden from view after the finish work. Secondly, I like the time you take in explaining the point, or lesson, you set out to show in your videos. Very impressive. Very Professional.
@BenjaminSahlstrom
@BenjaminSahlstrom 4 года назад
Here are some hand tools that I highly recommend: www.amazon.com/shop/benjaminsahlstrom Really appreciate all of your comments and the discussion here! Let me know what thoughts you have! If you use one of tha above links it will also help support the channel at NO cost to you. I wouldn't be able to do this without you guys. Blessings, Ben
@bartofilms
@bartofilms 4 года назад
Hey Ben, Thanks for sharing your knowledge. RU-vid channels like yours have given me the courage to take on many DIY projects. Cheers.
@rodrigjose
@rodrigjose 5 лет назад
thank you for the video, good explanation, be trying to find something like this.
@georgefeliz7875
@georgefeliz7875 4 года назад
I love to see young people with brains and using it. God bless you young man keep up the good work!
@edwrd1990
@edwrd1990 6 лет назад
This video was articulated surprisingly well. Btw, another reason why you wanna have separate breakers is for troubleshooting different floor levels. Plus, depending on your region’s code you might have a limit on how many light fixtures you can put on it.
@chapin-zo9ku
@chapin-zo9ku 3 года назад
4 years later we still watching your video 2020. Thank you!!!
@nikkiinthed7234
@nikkiinthed7234 6 лет назад
So far the best simple explanation I've watched. Thanks. Hope u have more videos!
@mccslawg
@mccslawg 5 лет назад
Thanks Ben for breaking this down in a way I can understand
@jimbola77
@jimbola77 7 лет назад
excellent video kid thank you for sharing love your vid's home to see some more coming!!!!
@clarkgriswold2480
@clarkgriswold2480 4 года назад
Wow. So many questions answered in one video. Thanks, man!
@romanocabrera8946
@romanocabrera8946 4 года назад
I am impressed with your web or youtube learning show about electrical instruction install. I am very much going to be following you with questions almost about anything in terms of electricity 101. Very good show i give it a thumbs up.
@johnm4579
@johnm4579 4 года назад
Good information bro for the novice. I like how you've spelled it out.
@coffeeisgood102
@coffeeisgood102 2 года назад
I switched my entire house to LED several years ago. Big saving. Your tutorials are always informative. Keep them coming.
@daringdarius
@daringdarius 3 года назад
Man you're my favourite guy to learn from! Quick, concise, and super knowledgeable. Keep it coming dude, love the videos!
@leistico
@leistico 3 года назад
When I was taught that calculation (in stagecraft class, for figuring cabling and dimmer loads), we called it the West Virginia formula. West Virginia The abbreviation for the state, before two-letter postal abbreviations, was W.Va W VA W = V times A. Easy little memory tool for remembering.
@joee7626
@joee7626 4 года назад
Well done! A clear and concise explanation with a good amount of relevant supporting information.
@lmc333
@lmc333 2 года назад
Thank you for this clear, easy and straight to the point video !! Safety is extremely important and you gave us all the main tips... Awesome starter video on this topic...
@keklordgrey4522
@keklordgrey4522 6 лет назад
cool... good job and good luck with the house! Was kinda watching 5 or 6 other guys... you broke down an hour vid into 4 minutes. Cheers!.
@jeffmykytiuk5642
@jeffmykytiuk5642 8 месяцев назад
Every time I watch one of your videos, I learn so much! I am a public school teacher and I can honestly say that you are a true teacher!
@theapotheosisofgdot2294
@theapotheosisofgdot2294 7 лет назад
Dude this is the best explanation I've seen on RU-vid so far... thanks for helping us newbies
@7381366
@7381366 6 лет назад
TheApotheosis OfGDot I agreee!!
@CASH-TO-THE-MERE101
@CASH-TO-THE-MERE101 4 года назад
TheApotheosis OfGDot 👍👍
@rockytoptech1308
@rockytoptech1308 2 года назад
Totally agreed!!! This is so perfect I had to subb this channel and save the vid in my "awesome electrical facts" folder 📂!!!
@GRATEFULLY.MrJones
@GRATEFULLY.MrJones 4 года назад
Well done! I appreciate the well explained answer.
@gregrichard9192
@gregrichard9192 4 года назад
Finally I understand this calculation. Great job 👍
@BigPlaneFixer
@BigPlaneFixer 3 года назад
Best and easiest explanation!!! Appreciate the math and the "dumbing" down for us non electricians. Now I know for sure I can add 3 LED's in my garage to my existing 2 light circuit which is 15 amps.
@KaioStryker
@KaioStryker 2 года назад
Agreed
@pp5237
@pp5237 6 лет назад
This came in handy today, thanks a lot. Good job!
@davidtoller137
@davidtoller137 6 лет назад
Excellent- succinct yet thorough and very helpful. Thanks!
@cifcig
@cifcig 5 лет назад
Ontario (Canada) building code allows up to 12 sockets & lights in one single circuit of a 15A in the living areas. Kitchen and washrooms are different because high power appliances are more likely used in these areas.
@ml9633
@ml9633 2 года назад
Thank you Ben. 2nd video of yours. Teach well and you are capable of breaking down complex to simple. Appreciate the way you make it easy and simple. Keep it up and thanks again, cheers, Maurice :)
@seanzafar120
@seanzafar120 3 года назад
Simple, brief and to the point video. Thank you!
@roadking6414
@roadking6414 3 месяца назад
Awesome, I needed a refresher. Thanks for the excellent tutorial!
@vincentfloyd4344
@vincentfloyd4344 5 лет назад
Once again it's your video that helps me out LOL thanks Ben :-)
@--JohnDoe
@--JohnDoe 6 лет назад
I was taught to use the fixture max wattage, if you did all fluorescent lights you would add up the bulb wattage plus the ballast efficiency right?
@isaiahkoldai8235
@isaiahkoldai8235 4 года назад
Really helpful bro, thanks for sharing your precious knowledge with us which we unable to source ourselves to appropriate people like you to acquire much informative life skills because of many reasons. Again thank-you very much, commenting from Papua New Guinea
@rockytoptech1308
@rockytoptech1308 2 года назад
Bruh you Sir are so EPIC for answering a question everyone has been seeking a simple explanation to!!! I'm now subbed and please keep the vids coming!!!! 🙏🏼😇
@BeeHiverson
@BeeHiverson 2 года назад
Thank you for the solid information sir!
@christopherduartelemus9158
@christopherduartelemus9158 2 года назад
Thank you sir for answering a question that not normally people look for continue the good work
@aquinojose94
@aquinojose94 5 лет назад
Wow! Thanks man! I love the theory education, can you explain arcing or burnt outlet?
@m.k.rahmathali9633
@m.k.rahmathali9633 5 лет назад
Yours explanation is very good & perfect & positive
@exclusivelynyc
@exclusivelynyc 3 года назад
Always providing excellent videos
@mangomadness8635
@mangomadness8635 3 года назад
Thank you for this great and relevant information. I love incandescent recessed lights. I just got mine installed.
@manofgod8672
@manofgod8672 5 лет назад
thank you for the video and information broken down
@dillonyoung5502
@dillonyoung5502 Год назад
Thanks got a project at the hall and they never sent me out to residential. Def worth subscribing
@dayarao1555
@dayarao1555 5 лет назад
Good explanation....simple with points...thank you
@aragoriluvatar5362
@aragoriluvatar5362 5 лет назад
Circuit 14 gauge wire (15A) (120V) = 1800W maximum contineuos load of a circuit is 80% = 0.8 multiplying (1800W) (0.8) = 1440W fixture wattage = 65W dividing 1440W / 65W = 22.15 lights 22 spotlights Thanks Ben
@CASH-TO-THE-MERE101
@CASH-TO-THE-MERE101 4 года назад
aragor iluvatar 👍👍👍👑👑👑
@glencaple3888
@glencaple3888 7 лет назад
Great tutorial.
@daveou8563
@daveou8563 7 лет назад
Great video. I've been looking all over the internet for this simple tutorial. Glad I stumbled upon your video. What if there are receptacles in the circuit, how much do they consume ? I would assume you subtract their wattage from the total.
@BenjaminSahlstrom
@BenjaminSahlstrom 7 лет назад
Dave Ou There aren't too many code requirements that I'm aware of for calculating that. Basically I'd consider two things: 1 - Are there any "anticipated continuous loads" that will be connected to said receptacles and if so you would include this in your 80% load. 2 - Other general purpose intermittent use receptacles don't need to be included in the calculation. I hope this helps a bit! The way I wired I didn't worry too much about the number of receptacles unless there were anticipated continuous loads involved. Use common sense and you'll be good. Thanks for your comment!
@BenjaminSahlstrom
@BenjaminSahlstrom 7 лет назад
Dave Ou Receptacles themselves don't consume any wattage. Only the items attached to them.
@annasmohammed4365
@annasmohammed4365 5 лет назад
It is recommended by IEC to connect receptacles/power load on separate circuit and lighting load on separate circuit. We should not connect both receptacles and lighting load on any single circuit. We should make separate circuit for each of them.
@juanchavez9153
@juanchavez9153 4 года назад
You have to size it to the max watts on each lights because you have to make it dummy prove.
@juanchavez9153
@juanchavez9153 4 года назад
ANNAS MOHAMMED brother I am from LA came to Bakersfield CA, I work for a company that connects lights and outlets together I spoke to the supervisor and told then not to mix and outlet and lights together and she said have you done electrical before I told her yes and she said what type I said commercial and custom homes she said it’s different I said it’s different but it’s the same principle and she said well the inspector don’t say anything are you saying he doesn’t know anything I say I am not saying that although I was😁 anyway after that talk they didn’t need my services and I was happy cuz they was putting like 18 outlets and lights together overloading the breaker putting so much resistance on a 14/2 wire that may cause 🔥
@fernandoullaguari9073
@fernandoullaguari9073 3 года назад
You are the best. I really like your videos. No bs straight to the point.
@JRH2830
@JRH2830 3 года назад
You explain everything very well and you really know what u are doing keep making more videos.Thanks
@rahj1365
@rahj1365 4 года назад
This is gold! thank you!!
@LisaMontgomery79
@LisaMontgomery79 4 года назад
Great explanation, concise and informative. Thank you.
@oscarortiz1114
@oscarortiz1114 3 года назад
Very well explained video. Thank you.
@Dave-nk6qz
@Dave-nk6qz 4 года назад
Great job Ben
@willwyatt7023
@willwyatt7023 3 года назад
Great, short video that answers the question VERY well.
@Shela100100
@Shela100100 6 лет назад
Awesome explanation!! Thanks
@aidendamien
@aidendamien 5 лет назад
Man, you are just AWESOME!!!
@coreygrua3271
@coreygrua3271 3 года назад
Practical, useful, and even interesting. Thank you!
@ZeenaIqbal
@ZeenaIqbal 4 года назад
Thank you for explaining it the way u did..
@RubiksRobo2
@RubiksRobo2 4 года назад
Ben you are the best... very detail information easy to understand . Good job
@downhill240
@downhill240 6 лет назад
Fine explanation! Thanks for sharing.
@Vamo_Alla
@Vamo_Alla 4 года назад
Hello, Great video and explanation!!! I’m having a situation now, i got a new washer machine 10 amps and when I plug 🔌 it the outlet sparks ⚡️. it only sparks when I plug the washer. I understand it has the most amps compare to the others appliances where I have it located. Also it is plugged to a gfci outlet. Now let me tell you about the breaker where i plug it. It is a 20 amps breaker and I noticed that breaker supply my refrigerator 6.5 amps and another outlet which I use it to charge cellphones and and 1 led light with low amps as well. Now when I use the washer machine, only the refrigerator is pulling amps and the rest are unplugged. Do you think is the refrigerator plugged in the same outlet causing the sparks ? Even though the outlet are separated but coming from the same 20 amps breaker. Sorry if this is too much writing and hope I won’t confused you. Thanks!!
@steveincollins
@steveincollins 3 года назад
What a great video! Very clear and informative 👌 👍
@mummymountainindica6646
@mummymountainindica6646 4 года назад
Good Explanation...Keep up the good work.
@BenjaminSahlstrom
@BenjaminSahlstrom 4 года назад
Thanks! Subscribe & hit the bell if you haven't yet as I have more electrical videos coming soon!
@Bluecollarworkingman
@Bluecollarworkingman 5 лет назад
Informative and clear enough.
@chrisstratton987
@chrisstratton987 4 года назад
B, Excellent presentation! Thank you!!!
@BenjaminSahlstrom
@BenjaminSahlstrom 4 года назад
Thanks! Subscribe if you haven't yet!
@rehmathanif7956
@rehmathanif7956 Год назад
You make great videos! Keep it up Thank you!
@TheJeffWay
@TheJeffWay 11 месяцев назад
very straightforward and easy to understand - thank you!
@jerylcarter330
@jerylcarter330 7 лет назад
great breakdown
@KevinCoop1
@KevinCoop1 4 года назад
Benjamin, A few finer points about this. Recess lights wattage used must be based on the maximum wattage that the trim will allow. Watts and va are the same for incandescent lamps, but are not the same for fluorescent, HID, or LED. For these fixtures always use VA(listed amps x listed voltage). As a designer, I never use the maximum number of fixtures. I leave enough room on circuits that if a few lights need to be added, it can be accomplished with existing circuits.
@felipetelleztorres967
@felipetelleztorres967 5 лет назад
Muchas Gracias Señor Benji for your good teachings is very helpful thanks👍🏻
@nelnolan8434
@nelnolan8434 4 года назад
Good refresher course for me. Very simplified explaination on why 's..
@IVAN2233
@IVAN2233 3 года назад
Nice and great explanation!!
@sergiom.6154
@sergiom.6154 4 года назад
Thanks bro. Just what I was looking for.
@UITNow
@UITNow 4 года назад
Excellent video! Good job Ben.
@jnicksnewstart
@jnicksnewstart 3 года назад
You have a really great ability to convey the subject to your viewer. You're articulate and easy to understand. My girlfriend has a 3600 square foot house built by KB in 2005. While I'm relatively sure that the wiring meets code, it seems to be the bare minimum at best. It's amazing how many receptacles and ceiling lamps are mixed on a single 15A circuit. If two people plug in a small electric heater in their bedrooms, it will trip the breaker and half the second floor goes dark. Also, it has the thinnest 14 gauge wire I have ever seen in my entire life. I had to do a double-take the first time I saw it. It might have been marked 14-2, but I compared it visually to a piece of scrap 14 THHN laying in the bottom of my pouch. The actual wire was considerably thinner. No kidding! This stuff looks like mismarked 16-gauge! No way that shit is made in this country. One other thing to remember when calculating ceiling circuits, is a lot of people are adding illuminated ceiling fans where there used to be just a single light in the middle of the room. The codes are written as the "minimum" accepted. I think it's worth a little time and money in the long run to use better materials and use fewer receptacles on each circuit. Best of luck. Stay safe, healthy and happy.
@russellcastillo5531
@russellcastillo5531 4 года назад
Thanks for halping. The explanation is so clear
@BenjaminSahlstrom
@BenjaminSahlstrom 4 года назад
Glad you found it to be helpful!
@court2379
@court2379 2 года назад
Before watching it was thinking enter stage left LED lighting. All of them! I divide mine by rooms by level vs passages. So a two story house would have one for each level, and a third for the passages (hallways, stairs, etc.). This way if you are in a room and do something that trips the circuit, you are not in the dark finding you way back to the panel.
@PLaTerra
@PLaTerra 4 года назад
Nice and simple and very helpful- thx!
@richcatch8386
@richcatch8386 6 лет назад
Thanks dude. I learned something today.
@felagoran7076
@felagoran7076 3 года назад
Don’t learn from RU-vid!!
@negrovazques3229
@negrovazques3229 7 лет назад
Great video! Lots of great into. Thanks.
@miguelgomez7189
@miguelgomez7189 7 лет назад
very good explanation thank you.
@mikimiki195
@mikimiki195 3 года назад
Yes sir that’s how you explain quick and very informative
@RosieNow
@RosieNow 6 лет назад
thanks bro, very well explained
@derraswaderra6474
@derraswaderra6474 6 лет назад
thankfully be blessed
@cesarnadores6856
@cesarnadores6856 6 лет назад
well explained .. keep it going dude
@HardHeadMilitary
@HardHeadMilitary 2 года назад
We do lighting in 12, and usually split the house in 3 lighting circuits. Split downstairs into 2 lighting circuits and one upstairs, and each room gets a receptacle home run on its own
@patrickarchuleta9594
@patrickarchuleta9594 2 года назад
They have lied to you young man .Im impressed you have done your homework great job God bless you 🙏👍
@mugalahenry8097
@mugalahenry8097 4 года назад
Thanks for the info bro keep on keeping on..
@islandvoice8667
@islandvoice8667 4 года назад
Educational video awesome thanks for sharing your knowledge
@marktheunitedstatescitezen185
@marktheunitedstatescitezen185 3 года назад
Thanks you’re explaining is thorough !
@shanalearns4098
@shanalearns4098 3 года назад
Such an informative awesome video dude!
@goalie2998
@goalie2998 6 лет назад
Very sound logical explanation. If circuit space was a concern. I would have no issue bringing multiple home runs into a junction box, and tying into 1 breaker. But one thing to keep in mind. Particularly on lighting loads. If 1 circuit controls the entire home, or even 1 entire floor. If the breaker trips the entire area will be in the dark. Assuming its dark out. Nice video
@user-zf3zc9pn8l
@user-zf3zc9pn8l 4 года назад
Excellent video,my good friend! Thank you!
@keepinitreal551
@keepinitreal551 4 года назад
Great job explaining.
@royalcrownimplantdental1613
@royalcrownimplantdental1613 7 лет назад
Your audio was great! what did you use to record it?
@wilmercruz5491
@wilmercruz5491 4 года назад
Great video, thanks for sharing 👍
@brianf5871
@brianf5871 5 лет назад
Well done. Thank you.
@alpagano50
@alpagano50 Год назад
excellent job explaining, good about LED's that if you need to add a few extra lights later on that same circuit Led will work without overloading circuit....Under kitchen cabinet lighting is a good place...
@alexk7950
@alexk7950 3 года назад
thank you for the break down. also does that formula work for receptacles?
@trulymine
@trulymine 7 лет назад
great video!
Далее
Should You Be ONLY Using 12/2? When Can You Use 14/2?
9:27
Amazing weight loss transformation !! 😱😱
00:24
Can 15 Amp Outlets Be Used On A 20 Amp Circuit Breaker
8:13
LED Wafer light Warning!
4:43
Просмотров 158 тыс.
Identify Circuit Breakers when Panel is Not Labeled
7:24